connect2
Structural
- Dec 24, 2003
- 306
So doing a small, lower end, mass concrete pour, the section is a 1.4m x 1.4m x 50m beam with a standard C1 concrete 35Mpa, 280 kg/m3 type 10 cement with 120 kg/m3 slag. Sealed the exposed top, left the forms on and covered the whole thing with insulated tarps for 3 days. Through the weekend ambient temp varies from 18 to 25oC. Monday, three days later, it was hot and uncomfortable to stand on. Had no thermal couples but took readings after the form was removed and the concrete on the o/s face was +/- 42oC. Hot and I can only imagine what the temp was inside the beam. Cracking on the top of the beam followed all the stirrup lines.
Is there a question here?
Yes what are your thoughts of what's occurred? My first thought is that at the batch plant they didn't do the slag substitution? The concrete temp at time of placement was running 19.6oC to 23oC.
Is there a question here?
Yes what are your thoughts of what's occurred? My first thought is that at the batch plant they didn't do the slag substitution? The concrete temp at time of placement was running 19.6oC to 23oC.