Cell Pressure in Triaxial 4
Jalthi
Geotechnical
Aug 20, 2009
41
I am a naive in triaxial test and looking for your assistance. How do we select the cell pressure (or ?3) for a UU triaxial test? For example, for a clay sample at 10 feet deep (?sat = 125 pcf) and groundwater table at 6 feet:
?v = 10 * 125 = 1,250 psf
?v' = 1,250 – 4 * 62.4 = 1,000 psf
?h' = 1,000 * 0.4 (k0) = 400 psf
?h = 400 + 4* 62.4 = 650 psf
What would be the cell pressure in this case if I am planning a single point test? If I am running a 3-stage test, what are the appropriate cell pressures? Thank you.
Use the in situ confining stress as the confining pressure.
Ron, you have re-stated my question. What is the confining pressure in the above example?
I suggest that you find a copy of Bishops book on Triaxial testing. As Ron stated, you should use 400 psf (as you are using ko as 0.4. Typically it is 0.5. I would consolidate the sample under the vertical and horizontal effective stresses before running the test.
For UU use total stress, for CU use effective...
Considering the way k0 is calculated (it is not, it is estimated and could well be 1.0-1.5 for a heavily overconsolidated clay) I would use:
For lightly overconsolidated soil:
UU: ?3=650
CU: ?'3=400
For heavily overconsolidated soil:
UU: ?3=1250
CU: ?'3=1000
If you are going to run 3-stage tests, arrange your ?3 or ?'3 to include these values...
Do look at the Bishop & Henkel book...fascinating
