FireProtection2009
Mechanical
- Nov 30, 2009
- 5
We have a project that is a new apartment bldg that is NFPA 13 with residential sidewalls. I have someone that seems to think I have to be 8’ away from ceiling fans. I am using nfpa 13 section 8.10.7.2.1.7 and A 8.6.5.2.1.10 and my take is that I do not have to be 8’ away if I meet these code sections. We are using tyco LFII res sidewalls and they do not address it in there tech sheet so I went to the residential sidewalls section of nfpa 13. We are also setting deflectors at 10” down so I don’t see a fan being a obstruction anyway. Can someone please clarify if my interpretation is correct or I am wrong. Thank you.