Apr 13, 2021 #1 james64 Electrical Joined Oct 16, 2012 Messages 46 Location CA Hi everyone, I am learning CDEGS recently, I found out "there are defects in the grounding grid during simulation, Use the diagnostic tool for more information. Does any body experience this problem? Thank in advance!!
Hi everyone, I am learning CDEGS recently, I found out "there are defects in the grounding grid during simulation, Use the diagnostic tool for more information. Does any body experience this problem? Thank in advance!!
Apr 13, 2021 #2 jghrist Electrical Joined Jul 16, 2002 Messages 4,226 Location US Did you use SES-CAD? From SES-CAD, you can do network diagnostics to find out where the problem is. Upvote 0 Downvote
Apr 13, 2021 Thread starter #3 james64 Electrical Joined Oct 16, 2012 Messages 46 Location CA Hi jghrist, I appreciated for your reply. I did network diagnostic as per your comment. It show up as attached. Upvote 0 Downvote
Hi jghrist, I appreciated for your reply. I did network diagnostic as per your comment. It show up as attached.
Apr 15, 2021 #4 jghrist Electrical Joined Jul 16, 2002 Messages 4,226 Location US It looks like you have many conductors entered twice. Conductor #1 is in the same location as Conductor #2. You will have to go through and fix each one. Probably delete redundant conductors. Upvote 0 Downvote
It looks like you have many conductors entered twice. Conductor #1 is in the same location as Conductor #2. You will have to go through and fix each one. Probably delete redundant conductors.
Apr 15, 2021 Thread starter #5 james64 Electrical Joined Oct 16, 2012 Messages 46 Location CA Hi jghrist, I do not know how to thank you. Everything was OK now since your comments. Upvote 0 Downvote