Hers is a brief on the curve. See the reference to one mains cycle of 20ms meaning the graph is equally applicable to 50Hz systems!
best regards,
The Information Technology Industry Council (ITIC) curve, formerly known as the Computer and Business Equipment manufacturers Association (CBEMA) curve, describes the tolerance of equipment to voltage disturbances of all types.
The solid lines represent the maximum and minimum voltages that can be tolerated without malfunction plotted against time. For example, data processing equipment should tolerate an over-voltage of five times nominal supply for a duration of 100 ?s but only 20 % over-voltage for 10 ms. On the under voltage side, a complete loss of supply should be tolerated for up to 20 ms (one mains cycle) but for 100 ms the minimum retained voltage must be 70 % of nominal. The curve was originally produced to help users of IT equipment in resolving power quality problems with electricity suppliers. By standardising the requirements of equipment it became much easier to determine by
site measurement whether the supply was adequate or not.