The end user can't interpolate. However, there is a chance the manufacturer may be able to provide a special rating for you. Sometime equipment undergoes a single test to get both ANSI and IEC ratings. Since the standards don't precisely align, the equipment may exceed both standards but in different ways. During actual testing, the CB could have been tested at above 25 kA, but not all the way up to the next standardized rating. We recently had a voltage regulator where the manufacturer provided a special rating about 10 percent higher than the IEEE standard value.