jay156

Structural
Apr 9, 2009
104
I just looked at a first floor in a 60 year old house that is sloping, not toward the foundation walls, like you'd expect if there were settlement, but about mid-span of the joists. Looking at the joists from below, there didn't seem to be any very obvious deflection, but I suppose it might look worse from above than below.

I'm thinking the most probable cause is creep losses and under-sized joists. (They're 2x8's and an 11' span). What do you think? I've seen this once before and was kinda stumped then too. Thanks.
 
Replies continue below

Recommended for you

My house is about 70 years old and one span of joists has a longer span than the others. There is a noticeable sag in the joists. Just long term deflection on joists that are a little undersized.
 
If the put in the joists relatively green and they were loaded, they would develop a memory of the deflection experienced as they dried.

Could also be creep as previously mentioned.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
Agree..it's probably creep. Pull a string line on the joists (or if you're not old school, use a laser line) and you'll quickly see the deflection that you can't discern from just looking.
 