CAT XQ400-C15 w/ EMCP3.2

Status
Not open for further replies.

zzzztt302

Electrical
Jul 10, 2010
6
Does anyone know what the default (factory) settings would be for the CAT EMCP3.2 controller w/ respect to OV/UV,OF/LF etc.etc.

Thanks
Phil
 
Replies continue below

Recommended for you

The standard used to be rated voltage +/- 10%, frequency +/-5 Hz. Lately a lot of sets have been coming out with some strange settings, likely due to changes in staff at factory and getting rid of old timers.
 
LOL.............Thanks Mike.........I know where you are coming from. I managed to run across the manual w/ settings.

Thanks

Mike
 