LRPSTRIKER
Marine/Ocean
We operate and maintain a floating power plant consisting of three (3) 250KW Caterpillar (3406B) Diesel Gen Sets tied into our switchgear allowing us to run two or all three units together, the gensets each utilize a Woodward 2301A Loadsharing / speed control. We parallel these as needed (based on demand) to supply power for our mobile operation. Our #2 Gen started displaying the following symptom, when load is increased (example: engine room exhaust fan turned on) the Cycles will drop to 54Hz then swing to 65Hz and eventually stabilize at 60Hz. The voltage output is not changing during this event. The other condition we are encountering is that when Units #1 and #2 are in parallel both gen sets are mildly hunting in tandem. This is observed at the actuators and on the Ampere gauges. We do not see this when #2 is in parallel with #3. We thought we possibly had a fuel supply problem with #2, we changed out the injection pump, fuel pump, and prime pump. We are still seeing the same problems with #2 by itself as well as when it is paralleled with #1. Any advice would be greatly appreciated.