Hello there,
I open and take a look on your model.
I have two questions:
1. Do you have a reson to not make the restraints (for the column base) blocked on UX,UY,UZ,RX,RY and RZ?
(I notice you use only blocked UX,UY,UZ). From what I know it is mau better for structure to block all.
2. On the continuation of the idea it is better for structure to be jointed at the roof level, not recessed.
With this you will obtain less moment force and better response for the structure, also you can reduce the size
of the section of elements.
I notice the structure it is on seismic area, I work as well on seismic area but with Eurocodes 8 for this reason I
assume the input and the Load case are define correct for your seismic codes, also the Load Combination.
Looks much more easy on you code, we define in other whey and take different the seismic load and masses.
This are my comment for the moment. Hope are good information.
P.S.: I'm not an expert but this is what I know from the books, please if somebody have an different opinion
can comment free.