Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Capacity of SOG

Status
Not open for further replies.

dgkhan

Structural
Jul 30, 2007
322
The UDL capacity of slab on grade is equal to bearing capacity of soil?
 
Replies continue below

Recommended for you

If you had a very small slab and your limiting factor were your soil bearing capacity, that would be true...otherwise no.
 
CRSI hase a table of thicknesses and reinforcing for SOG's of varying capacities.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
You would be correct if the ENTIRE slab was loaded uniformly. However, this is impossible in practice (there will be aisles between loaded areas), and so the slab in the aisle will tend to bend upward (tension in the top of the slab), and greatly reduce what uniform load can be supported.

DaveAtkins
 
Not meaning to put words in Ron's mouth... but the limitation on size is likely due to the uniform bearing conditions required. This is not common in real life...