Hello panou et al
If you are intending to use 30KVAR for a 37KW motor, then you are seriously over correcting. Static correction should be limited to 80% of the magnetising current of the motor unless you are using a dedicated contactor for the capacitors. For a 37KW motor, I would expect the magnetising current to be in the order of 25 - 40% of the rated current of the motor, so I would expect that the correction should be in the order of 10-15KVAR.
I have seen many installations with static power factor correction applied to star delta starters and the capacitors switched by the main contactor. I suspect that the connection of the capacitors to the starter will reduce the transient supply impedance at the starter and would probably increase the magnitude of the current and torque transients that occur after the open transition. I also suspect that there may be problems if the capacitors are connected to the output side of the delta contactor as during the open transition, you have a current path through the motor winding, through the capacitor and if this was near full correction, there would be effectively a very low impedance from the series LC circuit and potentially a high voltage generated. Bearing in mind that the motor is not connected in delta under these conditions, the magnetising current would be 57% of the delta mag current and if the correction was 80% of the delta mag current, the resonat frequency would be below line frequency and this is not desirable. In fact IT IS DANGEROUS!!. This is only a problem if the capacitors are connected to the output of the delta contactor and only while both the delta and the star contactors are open.
I would recommend a separate contactor for controlling the capacitors. I would connect this to the input side of the delta contactor and I would close this contactor after the delat contactor is closed. You could use an auxiliary contact on the delta contactor to close the capacitor contactor.
Please check the required level of protection required for that motor. It is not appropriate to try to bulk correct the plant based on the state of that motor only unless there are a number of motors that all operate at exactly the same time.
Either use the appropriate amount of correction for each motor controlled in sympathy with each starter, or use a power factor control relay to control bulk capacitors.
Best regards,
Mark Empson