Dear Gentlemen,
Anyone with experience in capacitor bank sizing calculations? I have a 280KW Vane Type Compressor and it is to be powered by a 400KVA Cos=.80 Diesel Generator, however problems occured during our test run. Initial Star-to-Delta start up is fine until the pump reaches 11Bars and automatically stops. But during the auto start again, when the tank is still filled with 8Bars, then the starting really gets too much high current from the generator at times almost "killing" the genset, and so therefore, my control voltages for the relays is affected. Voltage errors occurs and everytime I have to re-start the compressor manually.
And for this, I suggested to use a capacitor bank having a 300KVAr capacity. From my calculation, I used:
Step1:
For Maximum Power Factor Correction = 100%
Required KVar to improve from .80 to Unity
Capacitor Bank Rating (KVar) = 300KW x .750 (Factor) = 225KVar.
Step2:
Required KVar to improve from 0.80 to .95
Capacitor Bank Rating (KVar) = 300KW x .0.421 (Factor) = 126.3KVar
Step3:
Required KVar to improve from 0.80 to .90
Capacitor Bank Rating (KVar) = 300KW x .0.266 (Factor) = 79.8KVar
From these values, I choosed the higher rating, 300KVar from ABB.
Can someone here has some other calculations? Suggestions?
Regards.....
Anyone with experience in capacitor bank sizing calculations? I have a 280KW Vane Type Compressor and it is to be powered by a 400KVA Cos=.80 Diesel Generator, however problems occured during our test run. Initial Star-to-Delta start up is fine until the pump reaches 11Bars and automatically stops. But during the auto start again, when the tank is still filled with 8Bars, then the starting really gets too much high current from the generator at times almost "killing" the genset, and so therefore, my control voltages for the relays is affected. Voltage errors occurs and everytime I have to re-start the compressor manually.
And for this, I suggested to use a capacitor bank having a 300KVAr capacity. From my calculation, I used:
Step1:
For Maximum Power Factor Correction = 100%
Required KVar to improve from .80 to Unity
Capacitor Bank Rating (KVar) = 300KW x .750 (Factor) = 225KVar.
Step2:
Required KVar to improve from 0.80 to .95
Capacitor Bank Rating (KVar) = 300KW x .0.421 (Factor) = 126.3KVar
Step3:
Required KVar to improve from 0.80 to .90
Capacitor Bank Rating (KVar) = 300KW x .0.266 (Factor) = 79.8KVar
From these values, I choosed the higher rating, 300KVar from ABB.
Can someone here has some other calculations? Suggestions?
Regards.....