Capacitor banks utilize group fusing. The fuse should have a time-current clearing charactersitic that lies below the time current case rupture probability characteristic of the capcitor units. THere are 4 zones defined by 3 such curves - Safe Zone, Zone 1, Zone 2 and Hazardous Zone. Finally there is a inrush current similar to a transformer which has to be indicated on the TCC.