Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Cantilever beam span to depth ratio question 1

Status
Not open for further replies.

teach_me

Structural
Joined
Oct 27, 2022
Messages
20
Location
PH
Dimensional limits for beams of special moment frames "ACI 18.6.2.1 (a) Clear span ℓn shall be at least 4d "

does the provision above apply to cantilever beams? suppose there's a continuous span of beams of 0.5m depth and ends
are cantilevered, does that mean i can't use the same 0.5m depth for 1.5m cantilever span at the edges?
 

Cantilever beams are not part of SFRS and the clause "ACI 18.6.2.1 (a) Clear span ℓn shall be at least 4d " iis not applicable for cantilever beams.

Pls look commentary R18.6—Beams of special moment frames

It is acceptable for beams of special moment frames to cantilever beyond columns, but such cantilevers are not part of the special moment frame that forms part of the seismic-force-resisting system..

However , some codes limits the cantilever beam length ( ℓn <2.0 m ) and for simple calculation ( ℓn < 1/3 ls, ls is backspan length ) Look your local code.









Tim was so learned that he could name a
horse in nine languages: so ignorant that he bought a cow to ride on.
(BENJAMIN FRANKLIN )

 