Below is a sketch of a service from a Customer owned 12.47kV-480V transformer. There exists another service that comes into this same building that feeds the 277V lighting loads. That total load is no more than 200Amps, 480V, 3-phase. This is being re-worked so that there is only one service. And the lighting circuits will be fed out of this larger transformer also.
There is a #3/0 EG ran with each of the #500's in parallel in 3" EMT conduits. 3/0 has an ampacity of 200A. So we have an ampacity of 1600A of wire running between the service entrance and the transformer.
The question is ... if we jumpered between the neutral bus and the ground bus at the service - we would have our 277V needed for lights and we could just re-feed those lighting panels directly. We realize we could install 4W transformers at the panels, but this would be the simplest way, but is it a Code violation?