Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

can we use copper pipe for chilled water system? 1

Status
Not open for further replies.

Giri85

Mechanical
Joined
Dec 22, 2014
Messages
4
Location
SG
Hi All,

We are doing air conditioning for ships and as per owner spec, the piping should be copper piping. Is it possible or allowable to use copper pipe. If its yes please let me know the advantages and disadvantages of using it.

Regards,
Giri
 
above 2", copper is a hell of an expensive commodity.

The answer is yes you can, the only difference if the pressure drop
 
Thanks for your reply Mr.cry22(Mechanical) . Yes I accept the cost of the pipe is quite expensive. But the owner is ready to pay. So we don't have any problem.

Regards,
Giri
 
Another thing to consider is galvanic corrosion. I would think you'd be insulating the HVAC piping anyway, but I imagine you'd want some level of protection against corrosion.
Not having experience with HVAC installations on ship either, hopefully someone with ship experience can weigh in on this factor.
 
Thanks for your reply Mr.dbill74.. :-)
 