offshorehvac
Hi Friends
I am reviewing load calcutions submitted by a vendor
Application is comfort HVAC for Living Quarter on an offshore Rig.
There are about 90 small rooms being served by a large common AHU
Vendor has divided the load for rooms into two groups
In group 1, about 40 rooms and in group 2 about 50 rooms are considered. Then psychrometric analysis is performed for each group using air flows and average SHR for each group. Once the psychrometric is done, vendor has added the flow and capacity to arrive at the total capacity of one AHU serving all the 90 rooms
My question is that
-Is the right way to do?
-Can we add the capacities or psychromteric analysis should be done for the one single AHU which will serve all the rooms
-I know SHR plays an important roll in equipment selection. When calculations are done for two groups, the RSHR for group -1 is 0.85 and for group-2 is 0.9. But when we consider all the 90 rooms as one system then the RSHR is about 0.879
If this is acceptable then it is OK, If not then What should be my comment on the vendor calculations?
Can we add SHR
My question is that
Can we add SHR