Bill
That's a good tip. Rewind for a lower voltage and increase V/F (to the possible max input V) when torque boost is needed. It's a possibility. Thanks.
zlatkodo
Current during slow speed (165 RPM) operation is 22 to 23.5 Amps.
Slow speed operating cycle is a 10 minute cycle with total of 64 seconds ON in 10 minutes.
But in 10 minutes, it is switched on almost every minute. (10 starts)
So in one hour, load duration for slow speed operation is 384 seconds (6 min, 24 sec).
This operation repeats 43 times in 8 hours.
In 8 hours, slow speed operates for 43*64 =2752 sec (46 min) with 43*10 = 430 starts
Rest of the duty cycle is operated in other two speeds about which I don't have the data. A whirlwind of action in tyre making.
I guess a VFD rated for 30 Amps minimum is needed.
Or the VFD won't work at all given the widely varying load cycle. What do you drive gurus think?
Muthu