Jun 27, 2025 #1 pavanchinni Electrical Joined Dec 12, 2014 Messages 1 Location IN Hi all can anyone guide me how to calculate the GPR at the gas pipeline nearest to the substation when a fault occurs in the substation.
Hi all can anyone guide me how to calculate the GPR at the gas pipeline nearest to the substation when a fault occurs in the substation.
Jul 1, 2025 #2 7anoter4 Electrical Joined Oct 5, 2007 Messages 2,904 Location IL If no OHLine is close then the GPR fades exponential with the distance.See, for instance, the attached table from ENA EREC S34 Vx=ρI/(2.pi().r).arcsin(r/x) Formula P6.3 [Annex B] Upvote 0 Downvote
If no OHLine is close then the GPR fades exponential with the distance.See, for instance, the attached table from ENA EREC S34 Vx=ρI/(2.pi().r).arcsin(r/x) Formula P6.3 [Annex B]