For anyone else who is still thinking about the transformer phase shifts that davidbeach described but who are still not fully understanding it, this paper explains it and makes the explanation clear with phasor diagrams and connection diagrams. The phase shifts are not the point of the paper, differential relay protection is. However, in order to explain his point, the writer gives us all we need to know about the possibilities of reconnection of transformers to get non-standard phase shifts as davidbeach describes. It definitely helped me.
for davidbeach: Any time I see someone say; "I'll stand behind my statement" in response to one of my posts, I get the impression that they think that I have disagreed with what they said. That is not the case here.
A few days ago, I was stuck on the question of why would a utility that is capable of supplying load current to a plant not want to allow parallel operation with the same plant having a 1:1 cogen capability. Your post of 25 Oct 23:45 gave me the idea that answered my question; the fault current contribution of the cogen to the utility system beyond the point of interconnect.
In the scenario that I offered, there is no technical reason not to parallel if you can afford to pay the economic cost of upgrading the utility's distribution substation(s) to a higher MVA interrupting rating. It's just a matter of cost. We agree on that point.
That being said, the OP has stated several times that his utility does not allow parallel operation and he has stated that he is in Asia, not the US. I'll bet he wishes that he had a utility that was from 'your world' where this would not be a question or a problem. However, 'his world' is obviously different. I was offering an idea of why that may be true.
Moving on...You have offered a good, cost effective, solution for the OP to eliminate the utility's concern about the cogen's contribution to utlity system fault current. The use of a significant, high impedance, reactor when operating in parallel with the utility would definitely allow sychronized operation when there is no power flow while protecting against increased fault current contribution to the utility from the plant (or visa versa).
However, it seems to me that the reactor would have to be dropped out of the circuit once there was power flow through the interconnect point or else there would be a significant voltage drop across the reactor proportional to the plant load. A simple way to do this would be a breaker in parallel with the reactor that closes and shorts the reactor when the cogen generator breaker opens.
Does this agree with your knowledge and experience or am I missing something (again)?