electricpete
Electrical
- May 4, 2001
- 16,774
We have had intermittent trips of the instantaneous only breaker (MCP) when starting a 60 hp motor (occurred twice in approx 20 starts).
It was discussed some here thread237-225193 although I will repeat some details:
motor: 60hp, 3600rpm 460vac, KVA Code G induction motor started DOL in combination starter
breaker: Cutler Hammer HMCP 100R3 instantaneous only breaker, set on tap setting G (900A rms).
In between these two trips, we have replaced the breaker, and the starter. (the two trips occurred with two different breakers installed and two different starters installed).
Following both occurences, we have checked the motor breaker and monitored motor starting current. We have probably a total of 15 monitored starts of the motor. Motor current never exceeded approx 1100Amps peak during the start. Breaker trip point was never below approx 900A rms (which corresponds to about 1300A peak).
One thing we noted during monitoring after the 2nd start was that the starter contacts did not close simultaneously, and sometimes bounced. Worst case time from first contact closing on any phase to last closing on any phase was ½ cycle – most < ¼ cycle. This did not occur in a sister motor. We did not see any increase in current associated with this phenomenon, but wondering if it could (depending on timing). Example of non-simultaneous closing is shown on first slide here where unit 2 is the motor that tripped and unit 1 is a sister motor. (we measured Vab and Vac).
Question: Do you think this type of contact bounce and non-simultaneous closing (<1/2 cycle total) can significantly increase the current during starting of a motor ?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
It was discussed some here thread237-225193 although I will repeat some details:
motor: 60hp, 3600rpm 460vac, KVA Code G induction motor started DOL in combination starter
breaker: Cutler Hammer HMCP 100R3 instantaneous only breaker, set on tap setting G (900A rms).
In between these two trips, we have replaced the breaker, and the starter. (the two trips occurred with two different breakers installed and two different starters installed).
Following both occurences, we have checked the motor breaker and monitored motor starting current. We have probably a total of 15 monitored starts of the motor. Motor current never exceeded approx 1100Amps peak during the start. Breaker trip point was never below approx 900A rms (which corresponds to about 1300A peak).
One thing we noted during monitoring after the 2nd start was that the starter contacts did not close simultaneously, and sometimes bounced. Worst case time from first contact closing on any phase to last closing on any phase was ½ cycle – most < ¼ cycle. This did not occur in a sister motor. We did not see any increase in current associated with this phenomenon, but wondering if it could (depending on timing). Example of non-simultaneous closing is shown on first slide here where unit 2 is the motor that tripped and unit 1 is a sister motor. (we measured Vab and Vac).
Question: Do you think this type of contact bounce and non-simultaneous closing (<1/2 cycle total) can significantly increase the current during starting of a motor ?
=====================================