It is important to note that pressure maintenance pumps (also called make-up pumps or
jockey pumps) are not required by NFPA 20. NFPA 20 provides requirements for jockey pumps
only when they are installed; however, some method of maintaining system pressure, other
than through the fire pump(s), should be provided.
snip
For systems that use the
underground piping for both domestic and fire protection purposes, the operating pressure
must be coordinated, and the domestic pumps can operate as pressure maintenance pumps.
Since pressure maintenance pumps are not required, this section was revised for the 2010
edition to indicate that valves and other components are not required to be listed. The suction
isolation valve no longer needs to be an OS&Y, and isolation valves are not required to be
supervised. These changes were made because failure of the pressure maintenance pump will
not compromise the fire protection features of the fire pump system. Therefore, the level of
protection required of a fire pump is not necessary for a pressure maintenance pump.