What is independent ? Not sure about your question .. Do you think the firewall is a seperate structure with seperate frame ?
The last picture you have posted is for a corner plot of attached bldgs and the sidewalls at property line shall be fire rated firewall . The same requirement is valid for the next bldgs..
Maybe it would be helpfull to look to the definition and requirements of firewall , Copy and paste from
- IBC 2018
FIRE WALL. Fully addressed in Section 706, one or more fire walls are building elements used to divide a single building into two or more buildings for the purpose of applying the allowable height, allowable area, and type of construction requirements of the IBC. In addition, a fire wall is selectively identified in the code as a means to serve a variety of purposes, including the use of horizontal exit separation as addressed in Section 1026.2.Starting at the foundation and continuing vertically to or through the roof, a fire wall is intended to fully restrict the spread of fire from one side of the wall to the other. Fire walls
are higher level fire-resistance-rated elements than both fire barriers and fire partitions.Because the concept of fire walls is to create smaller buildings within one larger structure,with the code regulating each small building individually rather than collectively, it is critical that a fire wall be capable of maintaining structural stability under fire conditions. If
construction on either side of a fire wall should collapse, such a failure should not cause the fire wall to collapse for the prescribed time period of the rating of the wall.
-EC 1992
1.5.2 Fire wall: A wall separating two spaces (generally two buildings) that is designed for fire
resistance and structural stability, and may include resistance to horizontal loading such that, in
case of fire and failure of the structure on one side of the wall, fire spread beyond the wall is
avoided.
- SNIP II-01-02-85
Summary for Russian text: The fire wall shall be supported on foundation and extend entire heght of the bldg, fire walls can be constructed on the frame of the bldg with non-combustible material .Fire walls shall extent min.60 cm above the roof attica.
I hope this post answers your question ..