Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Calculation of line inductance

Status
Not open for further replies.

thinker

Electrical
Aug 2, 2001
247
Working with power quality/harmonics control standard
IEEE 519-92 I found that Paragraph 8.5.3 states:" Typically,
the per-phase line inductance on a three-phase AC line can
be considered to be 0.3 microHenry per foot of line". When
using this for line impedance and short circuit calculation,
the above number seems to be way too high. It is not clear
how that number could be derived without referencing to the
type of the feeder. Is this really a magic number? Could anybody advise another source for estimation of line (cable) impedance?
 
Replies continue below

Recommended for you

In 8.5.2 states 600V and bellow
As a reference you can use "Element of Power System Analysis" by Stevenson
 
Resistance and reactance for 600V cables can be found in NEC-2000 Table 9. The value in IEEE-519 is conservatively high for calculations of voltage notching, but for fault current calculations, a high estimate is not conservative.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor