whisperinghill
Industrial
- Jul 22, 2007
- 8
If I have a 120v circuit with 10A and one with 16A which totals 26A. But when I calculate for required total BTU/hr for cooling CFM, it doesn't come out to what my conditions currently are.
But since both of the circuits have a common Nuetral, would the total amps for these 2 circuits be calculated as the total (26) divided by 2 X 1.73 or 22.5 amps?
Representing the total actual heat load in the room? Assuming no lights, people or other loads?
But since both of the circuits have a common Nuetral, would the total amps for these 2 circuits be calculated as the total (26) divided by 2 X 1.73 or 22.5 amps?
Representing the total actual heat load in the room? Assuming no lights, people or other loads?