May 21, 2004 #1 RUFUS2K Mechanical Joined May 21, 2002 Messages 28 Location US I have lab testing data that shows that an evaporator is doing 11900 BTUH of latent cooling. How do I convert that value into an amount of water produced by the coil. I need to size a drain for the evaporator assembly. Thanks!
I have lab testing data that shows that an evaporator is doing 11900 BTUH of latent cooling. How do I convert that value into an amount of water produced by the coil. I need to size a drain for the evaporator assembly. Thanks!
May 21, 2004 1 #2 imok2 Mechanical Joined Oct 21, 2003 Messages 1,311 Location US Rufus2k: Devide 11,900 btuh by 970 btu = 12.268 lbs/hr then devide by 8.33#/gal =1.47/gal hr. Upvote 0 Downvote
May 21, 2004 #3 imok2 Mechanical Joined Oct 21, 2003 Messages 1,311 Location US Rufus I forget to mention ...never reduce the line size smaller then the outlet of the pan connecter Upvote 0 Downvote