Calculating Lbs of water/hr from known latent cooling 1

Status
Not open for further replies.

RUFUS2K

Mechanical
Joined
May 21, 2002
Messages
28
Location
US
I have lab testing data that shows that an evaporator is doing 11900 BTUH of latent cooling. How do I convert that value into an amount of water produced by the coil. I need to size a drain for the evaporator assembly.

Thanks!
 
Rufus2k:
Devide 11,900 btuh by 970 btu = 12.268 lbs/hr then devide by 8.33#/gal =1.47/gal hr.
 
Rufus I forget to mention ...never reduce the line size smaller then the outlet of the pan connecter
 