Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CABLE VS. CONDUIT TO CONNECT MOTOR

Status
Not open for further replies.

polareng

Electrical
Joined
Nov 24, 2006
Messages
16
Location
US
I need to connect a 10HP, 3ph motor to contoller box. Do I have to use conduit or can I use cable? The run is less than 10ft. Am I bound by NEC 400.7 Uses Permitted? because it is not specifically Not Permitted per 400.8. I just find it hard to believe that this would not be allowed.
 
Agreed!

I would just say that transitioning from conduit to cable can be a bit of a pain because you have to provide a junction box to make the extra connections verses transitioning to liquid-tite and just pulling the wires straight through to the motor/etc.

Keith Cress
Flamin Systems, Inc.-
 
UL listed shielded motor lead cable for drive-motor leads is available from Pirelli, Okonite, and recently, Belden.

I believe that each is listed for open (non-conduit) installation under controlled conditions.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top