Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Cable spacing

Status
Not open for further replies.

cmathew

Electrical
Jan 13, 2009
2
Is there any derating factor that can be used when using 500MCM cables? I am currently running 27 cables to a breaker, but I would like to minimize the spacing to less than 100% spacing. IS this possible?
 
Replies continue below

Recommended for you

Sure, but it lowers the ampacity of the conductor and increase the number of conductor, resulting in more total space required. There is a reason that the ampacity in tray with proper spacing is higher than the ampacity in conduit.
 
Would you happen to know which table in the CEC would have these derating factors? I mean with respect to spacing?
 
Tables
1
2
3
4
5B
5C
5D
Rules
4-004
8-104
12-2210
26-142
42-008
42-016
Appendix B Notes on Rules
4-0004
8-104


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
There are hugh derating factors for adjacent AC cables. I recommend that you contact your manufacturer, ask for applicaiton engineering. They typically have models which they can use to give you a conservative estimate.

Benjamin Lanz
Past Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor