Cable Size
Newcomer2005
CA
Hi everyone,
I am new graduate in electrical, if my question is very simple please forgive me in advance.
I am looking at ontario Electrical safety code, Table 1.
It says for single conductor 300MCM cable the ampacity is 480A (85-90 celcius)
On table 2 it says for 300MCM not more than 3 conductors in cable or raceway the ampacity is 295 (85-90 celcius).
On table 5B correction factors for table 1 it says for 3 conductors in contact the derating factor is 0.85
The question is this :
I am expecting that according tables 1, and 5B on table 2 the ampacity for one multiconductor cable (1c-3#350 MCM) be 480*0.85= 408A not 295A. and why table 2 is needed at all if the procedure for calculation is right.
I think I am missing something between multiconductor cables and single conductors.
Any help and references would be highly appreciated.
Newcomer2005
Table 1 is for an individual conductor in free air. If you read some of the rules, this table also covers individual conductors with an aluminum jacket.
Table 5B is a correction factor when individual conductors are put together in free air.
Table 2 is for conductors inside a raceway or cable, or in other words when there's another jacket or conduit covering the individual conductors.
Basically, the difference between single conductors and conductors in a cable or raceway is that the heat from the conductors in a cable or raceway has to travel through another barrier before reaching free air and the cables are all together inside this insulating barrier.
LionelHutz,
What is the ampacity of these two cases:
1)One cable three conductors (1-3/c-300MCM) in pvc conduit
2)three 300MCM cables (3#300MCM in pvc conduit
Thanks and Regards,
Newcomer2005