Dear Mr. joji90 (Petroleum)(OP)20 May 22 14:06
"... I have a power cable running from the MCC room to an analyzer cabinet, .... pulled 10mm2 cable. #1. however after the switch , its reduced to 2.5mm2 since this portion of the cable was existing. #2. this section of the cable is only 5 mts. #3. Can someone tell me if this would be an issue wrt the tripping of the breakers in the MCC room or could there be any other issue? ..."
#1. From your dwg, I take it that the power flow is from MDB-1-01 F21 (F22) with cable size 10mm2, up to the switch. " after the switch , its reduced to 2.5mm2 since this portion of the cable was existing." The switch should be replaced by a breaker or fuses rated for 2.5 mm2 conductor. Attention: A switch does NOT protects the conductor.
#2. With the switch replaced by a breaker/fuses, it would protect the 2.5 mm2 conductor irrespective of the length. FYI: When there is a change of conductor size, a protective device (e.g. breaker or fuse but not switch) shall be provided to protect the smaller conductor.
3. The breaker which is of a much higher rating, would NOT protect the 2.5mm2 conductor. The small breaker rated for 2.5mm2 conductor would likely co-ordinate with the much higher rated breaker. Therefore, in general; no co-ordination issue.
Che Kuan Yau (Singapore)