The 4.16 KV system has an NGR, 5A continuous. For a ground fault in the zone of service transfomer secondary and 4.16 KV SWGR main breaker, that breaker will open. The transformer primary has only a fuse, which will not open for the small current. The fault will then persist and be alarmed, but will only be cleared eventually by pulling the primary fuse on the pole. The elevated phase to ground voltage on two phases would be 173%. I believe the 100% 5 KV cable is not proper and the next higher available 8 KV insulation level is required, between the service transformer and SWGR. Cable would be 3/c, armoured, jacketted, probably unshielded. Does anyone have similar experience?