Cable Gland Earthing 1

Status
Not open for further replies.

duki

Electrical
Joined
Apr 21, 2003
Messages
31
Location
US
Does anyone know what the IEC requirements are concerning the use of earthing tags on cable glands. Are they to be used in non-metallic enclosures or on medium and high voltage cables entering panels? Do they have to be used at all?
 
Hi

IEC60364 (BS7671 Requirements For Electrical Installations) requires that the metallic sheaths of cables are earthed, brass gland tags are the usual means of achieving this and ensuring that cable sheaths / armours are solidly earthed.

IEC364 does not apply to medium voltage.

Are you in the UK ?

_______________________________________
Regards -

Colin J Flatters
Consulting Engineer & Project Manager
 
No. My company has a project in South Africa. Although I could not find any such mandate in SA, I now have the IEC cross reference I needed. Thanks for all your great help.
 

Potentially related discussion at thread238-90301
 