There isn't a minimum distance, in fact many are close coupled, mounted direct onto the transformer tank. There is a maximum length of cables between the transformer and the C/B, based on whether they can be adequately protected by the 11kV O/C protection, as the 11kV winding is generally delta, LV star.
Regards
Marmite