As ppedUK said "if you are carrying out hand calculations" it is more complicate.
You have to keep in your mind the fact there is not a cable "rated current" but "a rated conductor insulation temperature ".
For XLPE, for instance, the maximum temperature for short-time is 250 oC and for indefinite time 90 oC.
First of all check the "short-circuit thermal stability".
You need to know: maximum short-circuit current [from the Utility in your connection point on the Grid). For short-circuit current calculation see IEC 60909 [if you have to state the current by yourself]. You need also the short-circuit protection clearing time [sec].
See:
Second, you have to check the steady state load current [current-carrying capacity].
You may calculate it following [for instance] IEC 60287, but better to take it from standards as [for instance] DIN-VDE 0298 or IEEE Std 835-1994.
There are many way to run a cable: underground, in duct banks, through cable trays-open or close, exposed to sun shine or not and so on.
It is important if there are other power cables or other heat sources as hot pipes in the vicinity.
For cable laid in the ground you have to now the specific soil thermal resistance, the depth and the load factor, any way.
Usually you don't need to check the voltage drop. But, for medium voltage system, if there are big induction motor [starting DOL for example] supplied through this cable, you may have
to check the voltage drop also and you have to start from the source transformer [at least].