Cable bus sequence values

rmalkemes

Electrical
Joined
Dec 21, 2002
Messages
2
Location
US
I have a 4000A cable bus using 7 sets of 1000kCM Al XHHN conductors. Can the positive and zero sequence R and X values be computed or is some experimental data required? If it's a pure computation, can someone point me to appropriate references to do the calculation?
 
In my opinion, it is like the transmission line parameter calculation where inductance Lx=2/10^7*ln(GMD/GMRx) H/m
For imperial units, see -for instance:
LINE&CABLE PARAMETER CALCULATION
 
The positive sequence can certainly be calculated, but it will be much simpler to find a table of resistance and reactance for aluminum conductors of the appropriate insulation and voltage. You can assume 1/7 of the value for a The zero sequence impedance will depend heavily on the ground path. Consult a reference such as Elements of Power System Analysis by Stevenson, et al. Cable manufacturers would be a good resource.
 