bab1, as addition to the other mails,I know that each manu
facturer has it's own calculation for the diferent types of
swithdoad,presented in the table form for convenience.
For example, Schneider Electric in it's catalog for PRISMA P swchb proposes for 1000 A 1 bar/per phase with cross-section 80x5 mm for IP < 30 and 2 bars/phase with cross-section 50x5 for IP>31 - for 35C, for the higher temp.up to 50C derate 12% for IP 20 and 15% for IP 54.
The max.distance between busbar support center will be 125 mm. for 1 busbar (80x5) for 52 kA/1s ( case IP < 30) and
275 mm for 2 busbars ( IP>31). The distance between centre lines of phases and neutral busbar 75 mm. Other cases are in the catalogue.