coolmedown
Mechanical
- Jan 19, 2005
- 4
I have a heating coil 138/115 Deg C flow & return temperatures, design conditions. It is only 2 weeks old and recently burst at a support strap connecting the the flow and return header.
Before the incident under low load condition the return temperature was going back at 40 deg C. Is this normal and ok?. The control valve was only approximatly 10% open during this time maintaining off coil conditions smothly.
The coil supplier doesnt think the water should be going back so low and has blamed this on the controls system.
I am trying to figure out the thermodynamics of the coil re LMTD etc...and figure out why the coil burst.
Please help!!
Before the incident under low load condition the return temperature was going back at 40 deg C. Is this normal and ok?. The control valve was only approximatly 10% open during this time maintaining off coil conditions smothly.
The coil supplier doesnt think the water should be going back so low and has blamed this on the controls system.
I am trying to figure out the thermodynamics of the coil re LMTD etc...and figure out why the coil burst.
Please help!!