In the USA dry pipe sprinkler systems are everywhere where heat is not available, to list the info you need for your report would be a few million pages long! Dry pipe sprinkler systems are the second most popular sprinkler system with a wet pipe system being number one. Our building codes require automatic sprinkler protection based on occupancy, building construction, square footage, number of stories, etc. These requirements are NOT waived if the building and or area is not heated. The number of sprinkler systems required is based on the occupancy and square footage of the building from 40,000 sq.ft. to 52,000 sq. ft. by NFPA 13. A 120,000 sq. ft. non heated warehouse would require a minimum of 3 dry pipe sprinkler risers with each system protecting 40,000 sq. ft. Occupancies examples can include parking garages, warehouses, industrial buildings, attics of hotels, power plants, etc etc.
I was in the insurance loss prevention side of the business for 30 plus years in New Jersey and I encountered dry pipe systems on a daily bases during my site inspections. I hope this helps.