TedEP:
Your arrangement is determinate and can be made to be stable, and can be erected in a stable fashion. But, there may be a slightly more efficient arrangement in terms of beam/girder sizing. Starting at the left reaction, call the reactions R1, R2, R3..., etc., and label the beams B1, B2, B3..., etc. Starting from the left; B1 cantilevers over R2 to a hinge point; then B2 is a short hanger; B3 cantilevers over R3 and R4, in both directions; B4 is a short hanger from R5, out to the hinge on the right end of B3. This will probably result in sightly lighter beams than your arrangement. And, the whole scheme may be partially defeated if you have to consider snow drifting and alternate live loading. In the U.S. we call this cantilever construction, in Canada they call these a Gerber Beam System. Search Gerber Beams on this forum for other discussions and a good paper on this subject.
Be careful placing beams on top of columns, the beams and columns tend to form a hinge laterally, at the col. cap and beam bearing pl. This joint must be strengthened or braced in some way. Also, be careful not to place a beam hinge point at the same location where a stl. jst. or perpendicular beam frames onto or into the girder. You can’t make all the connections work well, or at all.