Building Occupancy Category - Code Clarification

Status
Not open for further replies.

cmbyrd77

Structural
Aug 4, 2010
79
I have a bit of a quandary. I am doing a roof framing evaluation for a client that wants to install solar panels. Currently I am determining the design the loads on the existing structure. The project is for a small college and the facility that I am looking at is large and therefore probably has a capacity of over 500, bumping it up to a Occupancy Category III. However, with that being said, the portion I am looking at is a small bumpout that only houses a couple small classrooms, with much less than 500 occupants, putting it into a Occupancy Category II. I am curious to see what some of my other fellow professional's opinions are on this subject. Thank you for the help.
 
Replies continue below

Recommended for you

Is the portion you are looking at considered a completely separate compartment, i.e. it's own fire compartment?

I've heard of people using different classifications for different segments of a large facility when each segment was it's own fire compartment.

Don't ask for proof though. Never done it myself, just an old wives tale.
 
There is a CMU wall between the bump-out and the remaining portion of the facility, but I doubt it is a true fire wall. Especially because the joists are bearing on it.
 
Unless the area is structurally separated, the worst occupancy category applies to the entire structure. If a structure with higher occupancy category has exiting or other life safety systems that pass through a structure with a lower occupancy category, both structures need to be designed with the higher occupancy category. For code reference, see ASCE 7-05 section 1.5.1 or 2009 IBC section 1604.5.1(for risk categories see ASCE7-10 section 1.5.2 or 2012 IBC section 1604.5.1).
 