Brittle failure - not suitable for SDC C or above.

Status
Not open for further replies.

CCFCE

Structural
Jul 14, 2008
7
I am trying out Quick Anchor to design anchor bolts for a steel building per ACI Appendix D. In the output i am getting a value for tension and shear x and shear y, but each has the "Brittle failure - not suitable for SDC C or above." note. I can not see in appendix D what this is. Has anyone else seen this?
 
Replies continue below

Recommended for you

do you have any thoughts about what is the controlling factor that would make it ductile? I have been trying different s spacings and supplemental reinforcing conditions as well as f'c but doesn't seem to make much difference.
 
Sure-

It means that the bolt fails- not the concrete.
 
thanks. it finally occurred to me after i posted this. i was so caught up in the numbers and formulas that i wasn't paying attention.
 
so no matter how excessive the load is for concrete, it has to exceed the bolt? seems excessive, when you consider the 0.75 factor already included
 
am i correct in assuming that if the capacity of the concrete (50k) exceeds the actual load (46k), i still have to design the concrete up to the steel capacity (80k)? i want to be sure because i am having to increase the ftg sizes to make this happen, and i see no way to make @ 3' diameter caisson work at all
 
That is one option. The other option is to design the baseplate to yield before the concrete breaks. Note that the IBC and now ACI 318-08 have provisions that allow you to wave the "ductile" requirement if the concrete breakout strength is 2.5 times the demand.
 
the base plate is designed by the metal building supplier so i have no control over that. do you know what section of the IBC allows waive ductile if breakout is 2.5 times demand? is this in ACI 08 and not 05? i think 2007 CBC uses 2006 IBC which uses ACI 05 and not 08 thanks for your input
 
It is located in IBC 2006 1908.1.16 (see italicized portion of reference to D.3.3.5)

It was not in ACI 318-05. It has been placed in ACI 318-08
in Section D.3.3.6 (the 0.4 factor is just reciprical of 2.5)
 
Please note the 318-05 doesn't give you much guidance on using shear friction to boost your capacity. 318-08 does. It may be worth getting just for that.
 
thanks for the section. i had it right in front of me but didn't see it.
is shear friction added to appendix d in 08? i don't think CBC 07 which uses IBC 06 uses 318-08, so i don't know if that would be allowed.
 
The IBC doesn't specify a year for 318. See IBC 1901.2.
 