This section has always made me angry as its wording is just poorly written.
Four ways to read the "English" here:
[blue]Option 1[/blue]
When the veneer exceeds 30 ft., you have to support any brick above 30 ft.
(unless it is part of a gable "triangle" up to 38 ft., where you don't have to provide additional support....but let's ignore the gable condition)
If you don't have a gable end, then the 30 ft. limit requires you to support any brick above 30 ft. and at each story thereafter.
That means you'd have a 30 ft. height of brick off the foundation, then supports at each story thereafter including your roof level (i.e. every 15 ft. in your case).
[blue]Option 2[/blue]
When the veneer exceeds 30 ft., you have to support any brick above 30 ft. - supporting the brick at each story above it, unless you have a part that is a gable - up to 38 ft.
You could possibly read the intent here that short parapets that go a bit above 30 ft. don't need the support at the roof line as they are similar to the 38 ft. tall gable end.
If the parapets send you above 38 ft (or perhaps the average of 34 ft) then you'd have to add support at the roof.
[blue]Option 3[/blue]
Same as Option 1 but you only have to provide the support
at the next story above 30 ft. (using the exact language of the text).
Since you don't have a "next story" you don't need to provide support at a story that doesn't exist.
So your parapet, even up to 38 feet,say, would be OK...as long as there's not another "story" above you.
[blue]Option 4[/blue]
It's Friday and the writers of this text were obviously drunk when they wrote it so do whatever you want.
Check out Eng-Tips Forum's Policies here:
faq731-376