Brick veneer attachment IBC 2

Status
Not open for further replies.

PSUengineer1

Structural
Jun 6, 2012
151
I am familiar with brick veneer attachment requirements per IRC (residential). What section on the IBC (commercial) lists connection requirements for brick veneer attached to wood framing?
 
Replies continue below

Recommended for you

Are you looking for a prescriptive spacing or just the general requirements? I domt know off the top of my head if anything is explicitly stated in the masonry chapter. But I'd start there and I'd also check with ACI 530. They have an entire chapter on veneer. Someone else may know if it's hidden in one of the arch dominant chapters.
 
@mike: I am specifically after spacing of ties requirement. Thank you.
 
Section 1405.6 refers you to ACI 530. Corrugated ties are typically acceptable for residential but not commercial. There are cavity gap length restrictions (1" max) and load restrictions in compression.
 
Yes - IBC refers out to ACI 530 - there is an "Anchored Veneer" chapter there that specifies tie spacing.