saltukhan
Electrical
- Nov 8, 2009
- 16
as far as i know, it is more difficult to break lagging currents than break resistive currents. is it true? if it is true why? does it matter the lag of the current,?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
So very true.Skogsgurra said:It is also true that using capital letters in the beginning of a sentence is a good habit.
De-energizing a capacitive load poses even more challenges. Because the current waveform leads
the voltage waveform by 90°, the current is interrupted very close to its zero crossing when the
voltage is at its maximum absolute value....
A capacitive switching device must be designed to endure the thermal stresses caused by the
re-ignitions and restrikes. Some circuit breakers fail to meet this level of performance. This is
why switching devices used for capacitor switching must be designed specifically for that application.
In many cases, such devices have a higher transient recovery voltage rating than general-use circuit
breakers
The characteristic waveform of the recovery voltage is shown in Fig. 13.2. A
high frequency voltage oscillation, known as the 'transient recovery voltage'
(TRV), fluctuates about the power frequency recovery voltage waveform. Its
behaviour is determined by the circuit parameters and the associated rapid redistribution
of energy between the network component electric and magnetic fields.
If the power factor of the faulted circuit is high (i.e. resistance is a significant proportion
of the total fault impedance) then the circuit or power source voltage at
current zero will be low. At low power factors (predominantly inductive or capacitive
circuits) the circuit voltage at current zero will be high and result in a
tendency for the arc to re-strike. This is the basic reason why inductive and
capacitive circuits are more difficult to interrupt than resistive circuits. The circuit
breaker must, therefore, be designed to withstand the transient recovery voltage.
Whether or not the arc extinguishes after the first current zero depends upon
establishing adequate dielectric strength across the circuit breaker contacts faster
than the rate of rise of TRV and the peak TRV involved.
Lead and lag are very relevant to the question as shown above. DC circuits such as ignition coils are not representative of the principles of ac circuit interruption because DC circuits do not have a natural current zero.CompositePro said:I think that the leading or lagging issue is not at all helpful in understanding the difficulties in switching inductive loads. As Gunnar said, inductors store energy in their magnetic fields. There is a physical relationship between the magnetic field and the current through a coil (inductor). If a switch tries to interrupt an inductive current the energy in the magnetic field will keep the current going until there is no more energy in the magnetic field. If precautions aren't taken the energy is dissipated in the switch. If the energy in the inductor is sufficient, the switch will be damaged or destroyed.
Understanding how ignition coils and magnetos work would be very helpful to understanding the concept.