Depending on the size of the inductance and the current at the time it could be a
very high voltage spike.
The surge suppressor essentially shorts the spike and is faced with doing this until the voltage drops to below the trigger level. Depending on just where the suppressor is located, impedance wise, in the circuit, controls how much of the energy in the spike actually is dropped inside the spike suppressor. This is why they all have energy ratings.
If you are toasting suppressors you need to either get one with a higher energy rating or interpose some resistance between the suppressor and the source of the voltage spikes.
There are two places you can add resistance. If you add in series with just the suppressor and its connection to the network being protected, you essentially protect the suppressor while reducing protection of the network. You must balance this with the fact that the more the resistance the higher the voltage the protected area will experence.
Alternatively you can instead add resistance to the network. Again this will cause the suppressor to see less energy during an event but it also helps the protected area of the system too. This is the method used most effectively with smaller devices like a TV. The spike suppressor is on the device's side of the zip cord supplying the device's power. When the suppressor is tripped the 6 feet of zip cord becomes the series resistance that dissipates most of the transient's energy. The normal power load is not hampered with this zip cord resistance during normal operation.
In large power systems this "source resistance" can result in substantial heating or power waste and is sometimes problematic. Often though it is fine and you even get transformers and such helping with the same issue and in the same way as the zip cord.
If the transient is being caused inside the system and nearby, then it gets harder to use interposing resistance as a helper. Hence add a larger energy capacity suppressor and if you hit the maximum size available then you have to provide some form of interposing resistance.
Keith Cress
kcress -