JimmyJunior
Electrical
- Jan 6, 2007
- 17
Our campus type facility is supplied from a 15kV dual lineup circuit breaker arrangement. Each lineup is fed from it own 20MVA transformer. The two lineups are tied through a NO circuit breaker. Each line up has 15kV, 1200A circuit breakers protected by the usual 50/51 overcurrent protection scheme. We are using workhorse electromechanical relays (IAC).
Recently the plant engineering group was notified that a phase relay had a target flag showing (time delay flag) but the associated breaker did not trip. Our electrical engineer PE became alarmed that such an event had occurred. He was of the opinion that we should obtain the services of a competent service company to test the relays and breaker in question as soon as possible, if not sooner. Other engineers and experienced electrcians took an opposite point of view. They said that it was probably due to vibration. The PE said that this was a possibility but the possible consequences in case of a fault that is not cleared in time or at all, compelled us to take action.
The Plant Engineer ruled in favor of waiting until a convenient time could be set aside to test the breaker/relays; "Since nothing had happened...nothing probably would..."
It may be worth noting that the PE has over 20 years of experience in power systems analysis, runs our short circuit and protective devices studies and previously worked for a couple of utilities doing the same kind of work.
Recently the plant engineering group was notified that a phase relay had a target flag showing (time delay flag) but the associated breaker did not trip. Our electrical engineer PE became alarmed that such an event had occurred. He was of the opinion that we should obtain the services of a competent service company to test the relays and breaker in question as soon as possible, if not sooner. Other engineers and experienced electrcians took an opposite point of view. They said that it was probably due to vibration. The PE said that this was a possibility but the possible consequences in case of a fault that is not cleared in time or at all, compelled us to take action.
The Plant Engineer ruled in favor of waiting until a convenient time could be set aside to test the breaker/relays; "Since nothing had happened...nothing probably would..."
It may be worth noting that the PE has over 20 years of experience in power systems analysis, runs our short circuit and protective devices studies and previously worked for a couple of utilities doing the same kind of work.