nightfox1925
Electrical
- Apr 3, 2006
- 567
We have traditionally followed the breaker failure scheme such that associated lockout relays will initiate breaker failure through the 50BF. The 50BF has current level detectors to supervise the breaker failure initiation to verify true breaker opening. The 50BF then sets off the 62BF timer which will perform actual breaker tripping.
There is a proposal to wire the controls such that the 62BF will be ahead of the 50BF. The 62BF will be initiated by protection trips (lockouts, relays) and then initiates the 50BF after time out. They say it will be faster since the 50BF reset time will not be part of the total breaker failure clearing time.
Anybody who made a scheme similar to this? I will appreciate any comments.
Secondly, what is a typical current setting for the 50BF?
Thank you...
There is a proposal to wire the controls such that the 62BF will be ahead of the 50BF. The 62BF will be initiated by protection trips (lockouts, relays) and then initiates the 50BF after time out. They say it will be faster since the 50BF reset time will not be part of the total breaker failure clearing time.
Anybody who made a scheme similar to this? I will appreciate any comments.
Secondly, what is a typical current setting for the 50BF?
Thank you...