I have worked in the petrochem industry for a while where a double ended main-tie-main system is very common. Now that I am on a power job I keep hearing breaker and a half scheme. The two seem similar but could someone tell me the difference between a breaker and half scheme and a double ended main-tie-main system?

 
The breaker and a half scheme would be like the M-T-M scheme if you have only one load per side of the M-T-M and no feeder breakers. Three breakers & two loads = 1 1/2 breakers per feeder.
 
Thank you! That makes sense
 
It's commonly operated with all three breakers closed so a trip requires opening two breakers. Multiple sets of 3/2 can be applied between two source buses.
 