I have a question regarding a breaker and a half protection scheme. Please see the PDF sketch I have attached for reference.
This is the current set up we are looking at: A breaker and a half configuration with the Tie Breaker as a normal open point. The protection (drawn in blue) is in a summing set up and if a fault is detected a trip command is sent to both breakers in the protected zone. Eg a fault on Load 1 under normal operating conditions a trip command will be sent to both Breaker 1 and the Tie Breaker.
Now the problem I am running into is if Breaker 1 is out of service for maintenance or whatever, Breaker 1 will be open and the Tie Breaker will be closed supplying Load 1 and Load 2 from Bus 2 if there is a Fault on Load 1 Relay 1 will still have to be in service as Relay 2 will sum the fault to 0 and not trip.
I would like to be able to take both the Breaker and the relay out of service during the maintenance outage and have Relay 2 do some smart tripping. The constraints I am working with are the protection Relay has to be a SEL-351A relay so we only have one set of current inputs. I was trying to come up with some logic or alternate CT configuration that makes sense.
Has anyone else run into a similar situation what are your suggestions?
This is the current set up we are looking at: A breaker and a half configuration with the Tie Breaker as a normal open point. The protection (drawn in blue) is in a summing set up and if a fault is detected a trip command is sent to both breakers in the protected zone. Eg a fault on Load 1 under normal operating conditions a trip command will be sent to both Breaker 1 and the Tie Breaker.
Now the problem I am running into is if Breaker 1 is out of service for maintenance or whatever, Breaker 1 will be open and the Tie Breaker will be closed supplying Load 1 and Load 2 from Bus 2 if there is a Fault on Load 1 Relay 1 will still have to be in service as Relay 2 will sum the fault to 0 and not trip.
I would like to be able to take both the Breaker and the relay out of service during the maintenance outage and have Relay 2 do some smart tripping. The constraints I am working with are the protection Relay has to be a SEL-351A relay so we only have one set of current inputs. I was trying to come up with some logic or alternate CT configuration that makes sense.
Has anyone else run into a similar situation what are your suggestions?